Question 5

5.1-Explain-the-principle-of-mutual-induction-with-reference-to-transformers-NSC Electrical Technology Power Systems-Question 5-2022-Paper 1.png

5.1 Explain the principle of mutual induction with reference to transformers. 5.2 Single-phase transformers can be used to create a three-phase transformer unit. An... show full transcript

Worked Solution & Example Answer:5.1 Explain the principle of mutual induction with reference to transformers - NSC Electrical Technology Power Systems - Question 5 - 2022 - Paper 1

Step 1

Explain the principle of mutual induction with reference to transformers.

96%

114 rated

Answer

Mutual induction occurs when the magnetic flux of one coil cuts through the conductors of an adjacent coil, inducing an electromotive force (emf) into that coil without any direct electrical connection between them. This principle is fundamental in the operation of transformers, as it allows energy transfer between primary and secondary windings.

Step 2

List THREE characteristics of single-phase transformers that must be identical.

99%

104 rated

Answer

  1. Transformer ratio: The primary to secondary voltage ratio must be the same.
  2. Current rating: The rated current for both phases should match.
  3. Power factor: The power factor rating of the transformers should be consistent.

Step 3

Name the connection on the secondary side of a three-phase transformer that will create a neutral point.

96%

101 rated

Answer

The ‘Star’ (Y) connection on the secondary side of a three-phase transformer creates a neutral point, which allows for balanced load distribution. This configuration is essential for providing a reference point for voltages in the system.

Step 4

Discuss the main contributing factors for copper losses in transformers.

98%

120 rated

Answer

Copper losses in transformers are primarily caused by the internal resistance of the copper conductors. When current flows through the windings, the resistance leads to heat generation, which is proportional to the square of the current (I2RI^2R losses).

Step 5

Discuss the main contributing factors for iron losses in transformers.

97%

117 rated

Answer

Iron losses, also known as core losses, are mainly caused by eddy currents and hysteresis effects within the transformer core. Eddy currents are generated due to the changing magnetic field, which induces circulating currents, while hysteresis losses occur due to the periodic magnetization and demagnetization of the core materials as the magnetic flux reverses.

Step 6

Describe how insulation failure is controlled in dry-type transformers.

97%

121 rated

Answer

In dry-type transformers, insulation failure is typically controlled through the use of tubular radiators that facilitate airflow to cool the windings. This helps prevent overheating and the breakdown of insulation materials, ensuring reliable performance and safety.

Step 7

Differentiate between shell-type and core-type transformers with reference to the core.

96%

114 rated

Answer

A core-type transformer has limbs where the coils are wound around three limbs, whereas a shell-type transformer incorporates coils wound around the central section of the core. The core arrangement impacts the transformer's efficiency and magnetic performance.

Step 8

Describe how a balanced earth-fault relay protects a three-phase transformer.

99%

104 rated

Answer

A balanced earth-fault relay operates by monitoring the three-phase currents. Under normal conditions, the vector sum of the three phase currents equals zero. If there is an earth fault on one of the phases, the imbalance will cause the relay to detect a difference in current, which will then isolate the transformer from the supply to prevent damage.

Step 9

Calculate the secondary line current.

96%

101 rated

Answer

Using the formula: IL2=P3VL2cosθI_{L2} = \frac{P}{\sqrt{3} V_{L2} \cos \theta} For a load of 200 kW, VL2=400 VV_{L2} = 400 \text{ V}, and power factor cosθ=0.8\cos \theta = 0.8: IL2=2000003×400×0.8=360.84AI_{L2} = \frac{200000}{\sqrt{3} \times 400 \times 0.8} \\ = 360.84 \, A

Step 10

Calculate the secondary phase current.

98%

120 rated

Answer

In a star configuration, the phase current is equal to the line current: Iph2=IL2=360.84AI_{ph2} = I_{L2} = 360.84 \, A

Step 11

Calculate the apparent power.

97%

117 rated

Answer

Apparent power is given by: S=Pcosθ=2000000.8=250000VA(or250kVA)S = \frac{P}{\cos \theta} \\ = \frac{200000}{0.8} \\ = 250000 \, VA \, (or 250 \, kVA)

Step 12

Calculate the primary line current.

97%

121 rated

Answer

Using the formula: P=3VL1IL1cosθP = \sqrt{3} V_{L1} I_{L1} \cos \theta For the primary side: 200000=3×6000×IL1×0.8IL1=24.06A200000 = \sqrt{3} \times 6000 \times I_{L1} \times 0.8 \\ I_{L1} = 24.06 \, A