FIGUUR 3.6: Delta-ster-transformator Gegee: S = 120 kVA V_LS = 380 V af. = 0,9 nalopend Bepaal die: 3.6.1 Sekondêre lynstroom 3.6.2 Sekondêre fases stroom 3.6.3 I... show full transcript

Worked Solution & Example Answer:FIGUUR 3.6: Delta-ster-transformator Gegee: S = 120 kVA V_LS = 380 V af - NSC Electrical Technology Power Systems - Question 2 - 2017 - Paper 1

Step 1

Sekondêre lynstroom

96%

114 rated

Answer

Om die sekondêre lynstroom te bereken, gebruik die formule:

Is=S3×VLSI_{s} = \frac{S}{\sqrt{3} \times V_{LS}}

Hier is:

  • S=120 kVA=120×103 W S = 120 \text{ kVA} = 120 \times 10^3 \text{ W}
  • VLS=380 VV_{LS} = 380 \text{ V}

Berekening:

Is=120×1033×380182.46 AI_{s} = \frac{120 \times 10^3}{\sqrt{3} \times 380} \approx 182.46 \text{ A}

Step 2

Sekondêre fases stroom

99%

104 rated

Answer

Die sekondêre fases stroom kan bereken word deur die volgende formule te gebruik:

If=Is3I_{f} = \frac{I_{s}}{3}

Berekening:

If=182.46360.82 AI_{f} = \frac{182.46}{3} \approx 60.82 \text{ A}

Step 3

Insedrwying na die kliniek

96%

101 rated

Answer

Die insedrwying na die kliniek kan verkry word deur die kategorie van die vertragingstransformator te oorweeg en oor die behoefte aan 'n dikker draad. 'n Dikker draad is nodig om die groter stroom wat in die sekondêre kring vloei, te kan hanteer, wat 'n afname in die weerstand en 'n groter doeltreffendheid in die transformator toelaat.

Join the NSC students using SimpleStudy...

97% of Students

Report Improved Results

98% of Students

Recommend to friends

100,000+

Students Supported

1 Million+

Questions answered

;