4.1 Name THREE losses that occur in transformers - NSC Electrical Technology Power Systems - Question 4 - 2018 - Paper 1

Question icon

Question 4

4.1-Name-THREE-losses-that-occur-in-transformers-NSC Electrical Technology Power Systems-Question 4-2018-Paper 1.png

4.1 Name THREE losses that occur in transformers. 4.2 State TWO applications of a delta-star transformer. 4.3 State TWO functions of the oil used in transformers. ... show full transcript

Worked Solution & Example Answer:4.1 Name THREE losses that occur in transformers - NSC Electrical Technology Power Systems - Question 4 - 2018 - Paper 1

Step 1

4.1 Name THREE losses that occur in transformers.

96%

114 rated

Answer

The three losses that occur in transformers are:

  1. Copper losses (I²R losses): These occur due to the resistance in the windings when current flows through them.
  2. Iron losses: This includes hysteresis losses (energy lost due to magnetic hysteresis) and eddy current losses (induced currents that create heat in the core).
  3. Stray losses: These result from leakage reactance and parasitic capacitance in the transformer.

Step 2

4.2 State TWO applications of a delta-star transformer.

99%

104 rated

Answer

The delta-star transformer is commonly used for:

  1. Power distribution in commercial settings: It allows for the efficient transfer of power across long distances.
  2. Voltage step-down in industrial applications: It adapts high voltage from transmission lines to lower voltage suitable for use in factories.

Step 3

4.3 State TWO functions of the oil used in transformers.

96%

101 rated

Answer

The oil in transformers serves two major functions:

  1. Insulation: It improves the insulation within the transformer, preventing electrical arcing and enhancing safety.
  2. Cooling: The oil conducts heat away from the windings, preventing overheating during operation.

Step 4

4.4 Describe the operation of a transformer.

98%

120 rated

Answer

A transformer operates on the principle of electromagnetic induction. It consists of two coils of wire, known as the primary and secondary windings, wound around a magnetic core. When an alternating current flows through the primary winding, it creates a magnetic field that induces a voltage in the secondary winding. The voltage ratio between the primary and secondary is determined by the turns ratio of the coils: VPVS=NPNS\frac{V_P}{V_S} = \frac{N_P}{N_S} This allows the transformer to step-up or step-down voltages depending on the turn counts.

Step 5

4.5 Explain why transformers have a better efficiency in comparison to other machines.

97%

117 rated

Answer

Transformers are more efficient than many other machines due to several reasons:

  1. No moving parts: Transformers do not have mechanical components that can wear out, which minimizes mechanical losses.
  2. Electromagnetic energy transfer: They operate on efficient electromagnetic induction, resulting in less energy lost as heat compared to devices that rely on mechanical motion.

Step 6

4.6 State the purpose of the Buchholz relay in transformers.

97%

121 rated

Answer

The Buchholz relay is utilized in transformers to detect abnormal gas formation, which may indicate problems such as insulation failure. It provides an early warning by isolating the transformer from the supply if gas accumulation occurs, thus preventing extensive damage.

Step 7

4.7.1 Secondary phase voltage

96%

114 rated

Answer

To calculate the secondary phase voltage, we use the formula: Vphase=VL(S)3V_{phase} = \frac{V_{L(S)}}{\sqrt{3}} Given that: VL(S)=380 VV_{L(S)} = 380 \text{ V} Thus, Vphase=3803219.39 VV_{phase} = \frac{380}{\sqrt{3}} \approx 219.39 \text{ V}

Step 8

4.7.2 Transformation ratio

99%

104 rated

Answer

The transformation ratio (TR) is calculated using: TR=VPVSTR = \frac{V_{P}}{V_{S}} Substituting the values: TR=2200219.3910:1TR = \frac{2200}{219.39} \approx 10:1

Step 9

4.7.3 Number of secondary turns

96%

101 rated

Answer

To find the number of secondary turns (NSN_S), we can relate it to the primary turns using the transformation ratio: VPVS=NPNS\frac{V_{P}}{V_{S}} = \frac{N_{P}}{N_{S}} Given:

  • NP=1500N_{P} = 1500 turns
  • VS=219.39V_{S} = 219.39 V

Rearranging gives: NS=NPVSVPN_{S} = N_{P} \cdot \frac{V_{S}}{V_{P}} So, NS=1500219.392200149.58 turnsN_{S} = 1500 \cdot \frac{219.39}{2200} \approx 149.58 \text{ turns}

Step 10

4.8.1 Determine whether the transformer is a step-down or a step-up transformer.

98%

120 rated

Answer

The transformer with a turns ratio of 30:1 is categorized as a step-down transformer, since the primary side has more turns than the secondary side (NP>NSN_P > N_S).

Step 11

4.8.2 Describe why the transformer can be used for distributing electrical power for domestic and industrial uses.

97%

117 rated

Answer

Transformers allow for the efficient distribution of electrical power by stepping down high transmission voltages to lower, safer levels suitable for domestic and industrial use. The star-delta configuration enhances this capability by providing a neutral point for three-phase systems, ensuring balanced loads in various applications.