5.1.1 State whether this is a core-type or shell-type three-phase transformer.
5.1.2 State ONE adva... show full transcript
Worked Solution & Example Answer:Refer to FIGURE 5.1 below and answer the questions that follow - NSC Electrical Technology Power Systems - Question 5 - 2024 - Paper 1
Step 1
5.1.1 State whether this is a core-type or shell-type three-phase transformer.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
This is a core-type three-phase transformer.
Step 2
5.1.2 State ONE advantage of a shell-type transformer over a core-type transformer.
99%
104 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
One advantage of a shell-type transformer is that it is less prone to magnetic stray loss compared to a core-type transformer.
Step 3
5.1.3 State the configuration of the primary and secondary windings in FIGURE 5.1 above.
96%
101 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The configuration of the primary and secondary windings in the transformer is star-delta (or delta-star) configuration.
Step 4
5.1.4 Briefly describe the principle of operation of the three-phase transformer in FIGURE 5.1 above.
98%
120 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
When an alternating voltage is applied to the primary windings of the transformer, an alternating magnetic flux is established in the core. This flux links with the secondary windings, inducing an electromotive force (e.m.f.) of the same frequency. When the load is connected to the secondary windings, a current flows through it. Power is thus transferred magnetically from the primary to the secondary windings.
Step 5
5.2.1 Describe the effect that an increase in the load will have on the primary current of a transformer.
97%
117 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
An increase in the load will increase the secondary current, resulting in a more prominent primary current drawn from the supply.
Step 6
5.2.2 Name ONE function of the dielectric oil used in transformers.
97%
121 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The dielectric oil provides electrical insulation between the windings and the case, helping to provide cooling and preventing breakdown of the windings.
Step 7
5.2.3 Name TWO types of losses other than copper losses that occur in transformers.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The two types of losses include hysteresis losses and eddy current losses.
Step 8
5.2.4 Name and explain TWO cooling methods used for dry transformers.
99%
104 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Two cooling methods include:
Air Natural: Transformers are cooled by natural air flow around the transformer windings.
Air Forced: Transformers are cooled by air being forced through a fan above the windings.
Step 9
5.2.5 Compare conductor sizes between a single-phase transformer and a three-phase transformer for the same power.
96%
101 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The conductor size in a single-phase transformer is larger than that required for a three-phase transformer. For the same power, the conductor size for a three-phase transformer is 75% of what is needed for a single-phase transformer.
Step 10
5.3.1 Calculate the following: Line current of the load
98%
120 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
To calculate the line current, we use the formula:
IL=3×VL1×cosϕPtr
By substituting the known values:
IL=3×600×0.87300×103=331.82A
Step 11
5.3.2 Phase current of the load
97%
117 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The phase current can be calculated using the formula:
Iph=3IL
Substituting the values gives:
Iph=3331.83=191.58A
Step 12
5.3.3 Primary line current
97%
121 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
To find the primary line current, we use the formula:
IL1=3×VL1×cosϕP
Substituting in the values:
IL1=3×8×103×0.87300×103=24.89A
Step 13
5.4 Protection devices used with three-phase transformers are categorised in two categories, relay and switches. Name TWO protection relays used in three-phase transformers.
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
Two protection relays used in three-phase transformers are: