Question 4

4.1-Refer-to-FIGURE-4.1-and-answer-the-questions-that-follow-NSC Electrical Technology Power Systems-Question 4-2022-Paper 1.png

4.1 Refer to FIGURE 4.1 and answer the questions that follow. 4.1.1 State whether the phasor diagram represents positive phase sequence or negative phase sequence. ... show full transcript

Worked Solution & Example Answer:4.1 Refer to FIGURE 4.1 and answer the questions that follow - NSC Electrical Technology Power Systems - Question 4 - 2022 - Paper 1

Step 1

4.1.1 State whether the phasor diagram represents positive phase sequence or negative phase sequence. Motivate your answer.

96%

114 rated

Answer

The phasor diagram represents positive phase sequence because the direction of rotation is anti-clockwise (R-Y-B phase sequence). This is important as it indicates the sequence in which the voltages reach their maximum values.

Step 2

4.1.2 Determine whether phasor V_RN represents a line voltage or a phase voltage. Motivate your answer.

99%

104 rated

Answer

Phasor V_RN represents a phase voltage because it is the voltage between R (Line 1) and the neutral (N), while line voltage is measured between two phase conductors.

Step 3

4.2 Explain the term active power.

96%

101 rated

Answer

Active power, or real power, refers to the capacity of a circuit for performing work in a particular time. It is measured in watts (W) and is the power consumed by a load to perform useful work.

Step 4

4.3 Draw a diagrammatic representation of a four-wire three-phase star-connected system.

98%

120 rated

Answer

The diagram should show three phases (L1, L2, L3) connected to a neutral point (N), and clearly indicate each line and the neutral line.

Step 5

4.4 Refer to voltages and explain what happens in the distribution stage of the national power grid.

97%

117 rated

Answer

In the distribution stage, power is distributed to substations at high voltages (e.g., 22 kV) for efficiency. These voltages are then stepped down to lower levels (e.g., 380 V/220 V) for final distribution to consumers such as homes and businesses, reducing losses and improving safety.

Step 6

4.6.1 Phase current of the load.

97%

121 rated

Answer

The phase current can be calculated using the formula:

IPH=IL3I_{PH} = \frac{I_L}{\sqrt{3}}

Substituting the values:

IPH=153IPH8.66AI_{PH} = \frac{15}{\sqrt{3}} \\ I_{PH} \approx 8.66 A

Step 7

4.6.2 Impedance of the load.

96%

114 rated

Answer

The impedance can be calculated using the formula:

ZPH=VPHIPHZ_{PH} = \frac{V_{PH}}{I_{PH}}

Where

VPH=VL3=4003231.7VV_{PH} = \frac{V_L}{\sqrt{3}} = \frac{400}{\sqrt{3}} \approx 231.7 V

Thus,

ZPH=231.78.6626.8ΩZ_{PH} = \frac{231.7}{8.66} \approx 26.8 \Omega

Step 8

4.6.3 Phase angle.

99%

104 rated

Answer

The phase angle can be calculated using the formula:

cos(θ)=pf\cos(\theta) = pf

Thus,

θ=cos1(0.85)31.79\theta = \cos^{-1}(0.85) \approx 31.79^{\circ}

Step 9

4.6.4 Active power.

96%

101 rated

Answer

Active power can be calculated using:

P=3VLILcos(θ)P = \sqrt{3} V_L I_L \cos(\theta)

Substituting the values:

P=3×400×15×0.858834.6W8.83kWP = \sqrt{3} \times 400 \times 15 \times 0.85 \approx 8834.6 W \approx 8.83 kW

Step 10

4.6.5 Draw a diagram of a power-factor correcting-capacitor bank connected to the three-phase supply in FIGURE 4.6.5.

98%

120 rated

Answer

The diagram should show a capacitor bank connected in parallel to the load on the three-phase supply with proper labeling of phases and components.

Step 11

4.7.1 State TWO advantages of using the three-wattmeter method.

97%

117 rated

Answer

  1. It can measure both balanced and unbalanced loads.
  2. The power consumption of each phase can be determined.

Step 12

4.7.2 State ONE disadvantage of the three-wattmeter method.

97%

121 rated

Answer

Three wattmeters are required for an unbalanced load. The terminals of the load must be available to connect the wattmeters if no neutral line exists.

Step 13

4.7.3 Calculate the total power for the reading on W_1 = 450 W.

96%

114 rated

Answer

For a balanced load:

PT=P1+P2+P3=3×P1P_T = P_1 + P_2 + P_3 = 3 \times P_1

Thus,

PT=3×450W=1350W1.35kWP_T = 3 \times 450 W = 1350 W \approx 1.35 kW