Refer to FIGURE 4.1 and answer the questions that follow. 4.1 State whether the phasor diagram represents positive phase sequence or negative phase sequence. Motiva... show full transcript

Worked Solution & Example Answer:Refer to FIGURE 4.1 and answer the questions that follow - NSC Electrical Technology Power Systems - Question 4 - 2022 - Paper 1

Step 1

4.1 State whether the phasor diagram represents positive phase sequence or negative phase sequence. Motivate your answer.

96%

114 rated

Answer

The phasor diagram represents a positive phase sequence because the direction of rotation is anti-clockwise, indicating that the phases R, Y, and B follow each other in that order.

Step 2

4.1.2 Determine whether phasor Vrn represents a line voltage or a phase voltage. Motivate your answer.

99%

104 rated

Answer

Phasor Vrn represents a phase voltage because it is the voltage between R (Line 1) and neutral (N).

Step 3

4.2 Explain the term active power.

96%

101 rated

Answer

Active power, also known as real power, refers to the capacity of a circuit to do useful work over time, which is measured in watts (W). It represents the power consumed by resistive elements in an electrical circuit and is usually the power that is converted into work.

Step 4

4.3 Explain the effect of stepping up the voltage in transmission lines.

98%

120 rated

Answer

Stepping up the voltage in transmission lines reduces the current flowing through the lines, which minimizes power losses due to heat in the conductors. Higher voltage levels allow for more efficient long-distance electricity transmission, as lower current reduces the I²R losses.

Step 5

4.4 Draw a diagrammatic representation of a four-wire three-phase star-connected system.

97%

117 rated

Answer

A diagram for a four-wire three-phase star-connected system consists of three phases (R, Y, B) connected to a neutral wire. Each phase is connected to a load, and the neutral wire is connected to the star point where all phases meet.

Step 6

4.5 Refer to voltages and explain what happens in the distribution stage of the national power grid.

97%

121 rated

Answer

In the distribution stage, power is initially distributed at high voltages (like 22 kV) to reduce losses. The voltage is then stepped down to lower levels (such as 380 V/220 V) for supply to homes and businesses, allowing for safe and efficient delivery of electricity.

Step 7

4.6.1 Phase current of the load.

96%

114 rated

Answer

The phase current can be calculated using the formula: IPH=IL3I_{PH} = \frac{I_L}{\sqrt{3}} Substituting the values gives: IPH=15A38.66AI_{PH} = \frac{15 A}{\sqrt{3}} \approx 8.66 A

Step 8

4.6.2 Impedance of the load.

99%

104 rated

Answer

The impedance of the load can be calculated using: ZPH=VLIPHZ_{PH} = \frac{V_{L}}{I_{PH}} Given that V_L = 400 V: ZPH=400V8.66A46.19ΩZ_{PH} = \frac{400 V}{8.66 A} \approx 46.19 \Omega

Step 9

4.6.3 Phase angle.

96%

101 rated

Answer

The phase angle can be derived using the power factor (pf): θ=cos1(pf)=cos1(0.85)31.79exto\theta = \cos^{-1}(pf) = \cos^{-1}(0.85) \approx 31.79^ ext{o}

Step 10

4.6.4 Active power.

98%

120 rated

Answer

Active power can be calculated using: P=3VLILcos(θ)P = \sqrt{3} V_{L} I_{L} \cos(\theta) Substituting the values: P=3400V15A0.858833.46WP = \sqrt{3} \cdot 400 V \cdot 15 A \cdot 0.85 \approx 8833.46 W

Step 11

4.6.5 Draw a diagram of a power-factor correcting-capacitor bank connected to the three-phase supply in FIGURE 4.6.5.

97%

117 rated

Answer

The diagram will include a three-phase supply with capacitance connected in parallel with the load to correct power factor. Each phase will have a capacitor bank connected, labeled as C1, C2, and C3 for the respective phases.

Step 12

4.7.1 State TWO advantages of using the three-wattmeter method.

97%

121 rated

Answer

  1. It can measure both balanced and unbalanced loads.
  2. The power consumption of each phase can be determined individually.

Step 13

4.7.2 State ONE disadvantage of the three-wattmeter method.

96%

114 rated

Answer

One disadvantage is that three wattmeters are needed for unbalanced loads, which may complicate the measurement process.

Step 14

4.7.3 Calculate the total power for the reading on W1 = 450 W.

99%

104 rated

Answer

For a balanced load using the three-wattmeter method, the total power is given by: PT=P1+P2+P3P_{T} = P_{1} + P_{2} + P_{3} For three wattmeter readings, this can be expressed as: PT=3450W=1350WP_T = 3 \cdot 450 W = 1350 W