a) Calculate the U-value of the uninsulated concrete ground floor, given the following data: Sand/cement fine screed thickness 50 mm Concrete floor slab thickness 100 mm Radon barrier thickness 0.25 mm Sand binding thickness 40 mm Hardcore thickness 200 mm Subsoil thickness 300 mm Thermal data of the concrete ground floor: Resistance of internal top surface of floor (R) 0.104 m² °C/W Resistivity of fine screed 0.720 m² °C/W Conductivity of concrete floor slab 1.280 W/m °C Conductivity of radon barrier 0.250 W/m °C Conductivity of sand binding 0.160 W/m °C Conductivity of hardcore 1.350 W/m °C Conductivity of subsoil 1.600 W/m °C b) Using the U-value of the concrete floor obtained at 5(a) above and the following data, calculate the cost of heat lost annually through the uninsulated concrete floor slab: - dimensions of floor slab 6.0 metres x 12.0 metres - average internal temperature 21 °C - average temperature of subsoil 5 °C - heating period 10 hours daily for 38 weeks per annum - cost of oil 96 cent per litre - calorific value of oil 37350 kj per litre - 1000 Watts c) It is proposed to redesign the above floor and upgrade its thermal properties to meet the Passive House standard by including expanded polystyrene in the design of the floor - Leaving Cert Construction Studies - Question 5 - 2018

Question icon

Question 5

a)-Calculate-the-U-value-of-the-uninsulated-concrete-ground-floor,-given-the-following-data:--Sand/cement-fine-screed-thickness-50-mm-Concrete-floor-slab-thickness-100-mm-Radon-barrier-thickness-0.25-mm-Sand-binding-thickness-40-mm-Hardcore-thickness-200-mm-Subsoil-thickness-300-mm--Thermal-data-of-the-concrete-ground-floor:--Resistance-of-internal-top-surface-of-floor-(R)-0.104-m²-°C/W-Resistivity-of-fine-screed-0.720-m²-°C/W-Conductivity-of-concrete-floor-slab-1.280-W/m-°C-Conductivity-of-radon-barrier-0.250-W/m-°C-Conductivity-of-sand-binding-0.160-W/m-°C-Conductivity-of-hardcore-1.350-W/m-°C-Conductivity-of-subsoil-1.600-W/m-°C--b)-Using-the-U-value-of-the-concrete-floor-obtained-at-5(a)-above-and-the-following-data,-calculate-the-cost-of-heat-lost-annually-through-the-uninsulated-concrete-floor-slab:----dimensions-of-floor-slab-6.0-metres-x-12.0-metres---average-internal-temperature-21-°C---average-temperature-of-subsoil-5-°C---heating-period-10-hours-daily-for-38-weeks-per-annum---cost-of-oil-96-cent-per-litre---calorific-value-of-oil-37350-kj-per-litre---1000-Watts--c)-It-is-proposed-to-redesign-the-above-floor-and-upgrade-its-thermal-properties-to-meet-the-Passive-House-standard-by-including-expanded-polystyrene-in-the-design-of-the-floor-Leaving Cert Construction Studies-Question 5-2018.png

a) Calculate the U-value of the uninsulated concrete ground floor, given the following data: Sand/cement fine screed thickness 50 mm Concrete floor slab thickness 1... show full transcript

Worked Solution & Example Answer:a) Calculate the U-value of the uninsulated concrete ground floor, given the following data: Sand/cement fine screed thickness 50 mm Concrete floor slab thickness 100 mm Radon barrier thickness 0.25 mm Sand binding thickness 40 mm Hardcore thickness 200 mm Subsoil thickness 300 mm Thermal data of the concrete ground floor: Resistance of internal top surface of floor (R) 0.104 m² °C/W Resistivity of fine screed 0.720 m² °C/W Conductivity of concrete floor slab 1.280 W/m °C Conductivity of radon barrier 0.250 W/m °C Conductivity of sand binding 0.160 W/m °C Conductivity of hardcore 1.350 W/m °C Conductivity of subsoil 1.600 W/m °C b) Using the U-value of the concrete floor obtained at 5(a) above and the following data, calculate the cost of heat lost annually through the uninsulated concrete floor slab: - dimensions of floor slab 6.0 metres x 12.0 metres - average internal temperature 21 °C - average temperature of subsoil 5 °C - heating period 10 hours daily for 38 weeks per annum - cost of oil 96 cent per litre - calorific value of oil 37350 kj per litre - 1000 Watts c) It is proposed to redesign the above floor and upgrade its thermal properties to meet the Passive House standard by including expanded polystyrene in the design of the floor - Leaving Cert Construction Studies - Question 5 - 2018

Step 1

Calculate the U-value of the uninsulated concrete ground floor

96%

114 rated

Answer

To calculate the U-value, first determine the thermal resistances of each layer:

  1. Calculate the resistance: R=tkR = \frac{t}{k} where:

    • tt is the thickness
    • kk is the thermal conductivity.
  2. Resistance of each layer:

    • Sand/cement fine screed: 50 mm = 0.050 m
      • Rs=0.0500.720=0.0694 m2°C/WR_s = \frac{0.050}{0.720} = 0.0694 \ m^2 \degree C/W
    • Concrete floor slab: 100 mm = 0.100 m
      • Rc=0.1001.280=0.0781 m2°C/WR_c = \frac{0.100}{1.280} = 0.0781 \ m^2 \degree C/W
    • Radon barrier: 0.25 mm = 0.00025 m
      • Rr=0.000250.250=0.0010 m2°C/WR_r = \frac{0.00025}{0.250} = 0.0010 \ m^2 \degree C/W
    • Sand binding: 40 mm = 0.040 m
      • Rb=0.0400.160=0.250 m2°C/WR_b = \frac{0.040}{0.160} = 0.250 \ m^2 \degree C/W
    • Hardcore: 200 mm = 0.200 m
      • Rh=0.2001.350=0.1481 m2°C/WR_h = \frac{0.200}{1.350} = 0.1481 \ m^2 \degree C/W
    • Subsoil: 300 mm = 0.300 m
      • Rsu=0.3001.600=0.1875 m2°C/WR_su = \frac{0.300}{1.600} = 0.1875 \ m^2 \degree C/W
  3. Total resistance RtotalR_{total}: Rtotal=Rs+Rc+Rr+Rb+Rh+RsuR_{total} = R_s + R_c + R_r + R_b + R_h + R_su Calculate: Rtotal=0.0694+0.0781+0.0010+0.250+0.1481+0.1875=0.7341 m2°C/WR_{total} = 0.0694 + 0.0781 + 0.0010 + 0.250 + 0.1481 + 0.1875 = 0.7341 \ m^2 \degree C/W

  4. Finally, the U-value can be calculated as: U=1Rtotal=10.73411.363 W/m2°CU = \frac{1}{R_{total}} = \frac{1}{0.7341} \approx 1.363 \ W/m^2 \degree C

Step 2

Using the U-value of the concrete floor obtained at 5(a) above, calculate the cost of heat lost annually through the uninsulated concrete floor slab

99%

104 rated

Answer

  1. Heat loss formula: Q=UAΔTQ = U \cdot A \cdot \Delta T

    • Where:
      • UU is the U-value
      • AA is the area
      • ΔT\Delta T is the temperature difference.
  2. Calculate the area: Area = 6.0 m x 12.0 m = 72 m²

  3. Given:

    • Average internal temperature: 21 °C
    • Average temperature of subsoil: 5 °C
    • ΔT=215=16°C\Delta T = 21 - 5 = 16 °C
  4. Substituting values: Q=1.3637216=1432.3968 WattsQ = 1.363 \cdot 72 \cdot 16 = 1432.3968 \text{ Watts}

  5. Convert heat lost per day: Qperextday=1432.3968×10 hours×38 weeks×7 days=9,576,000 JoulesQ_{per ext{ day}} = 1432.3968 \times 10 \text{ hours} \times 38 \text{ weeks} \times 7 \text{ days} = 9,576,000 \text{ Joules}

  6. Convert to kilojoules: 9,576,000 Joules=9,576 kJ9,576,000 \text{ Joules} = 9,576 \text{ kJ}

  7. Cost calculation:

    • Cost of oil = 96 cents per litre
    • Calorific value = 37350 kJ/litre

    extLitres=9,57637,3500.256 litres ext{Litres} = \frac{9,576}{37,350} \approx 0.256 \text{ litres}

    • Cost per annum = 0.256 x 0.96 * 1000 = € 245.76 annually.

Step 3

Calculate the thickness of expanded polystyrene required to achieve a U-value of 0.15 W/m²°C

96%

101 rated

Answer

  1. Given:

    • Current U-value: 1.2434 W/m²°C
    • Desired U-value: 0.15 W/m²°C.
  2. Use the formula: U=1RtotalU = \frac{1}{R_{total}} Rtotal=1UR_{total} = \frac{1}{U} Rtotal=10.15=6.6666 m2°C/WR_{total} = \frac{1}{0.15} = 6.6666 \ m^2 \degree C/W

  3. Calculate the total resistance of layers, including expanded polystyrene: Rtotal=Rs+Rc+Rr+Rb+Rh+Rsu+RpolystyreneR_{total} = R_s + R_c + R_r + R_b + R_h + R_su + R_{polystyrene}

  4. Assuming all other resistances remain constant, solve for RpolystyreneR_{polystyrene}: Rpoly=6.6666(Rs+Rc+Rr+Rb+Rh+Rsu)R_{poly} = 6.6666 - (R_s + R_c + R_r + R_b + R_h + R_su)

  5. Substitute each layer's resistance: Rpoly=6.66660.73415.9325 m2°C/WR_{poly} = 6.6666 - 0.7341 \approx 5.9325 \ m^2 \degree C/W

  6. Calculate thickness: Rpolystyrene=tkt=Rpolystyrene×kR_{polystyrene} = \frac{t}{k} \Rightarrow t = R_{polystyrene} \times k(k for polystyrene is 0.037) t=5.9325×0.037=0.219 m=219mmt = 5.9325 \times 0.037 = 0.219 \text{ m} = 219 mm

Thus, thickness required is approximately 216/217 mm.

Join the Leaving Cert students using SimpleStudy...

97% of Students

Report Improved Results

98% of Students

Recommend to friends

100,000+

Students Supported

1 Million+

Questions answered

Other Leaving Cert Construction Studies topics to explore

Condensation & Air Tightness

Construction Studies - Leaving Cert

Conservation & Restoration

Construction Studies - Leaving Cert

Doors

Construction Studies - Leaving Cert

Drainage

Construction Studies - Leaving Cert

Fireplaces & Fire prevention

Construction Studies - Leaving Cert

Floors

Construction Studies - Leaving Cert

Foundations

Construction Studies - Leaving Cert

Heat & U-Value Calculations

Construction Studies - Leaving Cert

Heat Loss & Insulation

Construction Studies - Leaving Cert

Hot Water & Space Heating

Construction Studies - Leaving Cert

Passive Design

Construction Studies - Leaving Cert

Planning, Sustainability & Environment

Construction Studies - Leaving Cert

Question 1: Drawing Questions

Construction Studies - Leaving Cert

Roofs

Construction Studies - Leaving Cert

Services: Water, Gas, Electricity

Construction Studies - Leaving Cert

Site Safety

Construction Studies - Leaving Cert

Sound

Construction Studies - Leaving Cert

Stairs

Construction Studies - Leaving Cert

Sustainability & the Environment

Construction Studies - Leaving Cert

Walls

Construction Studies - Leaving Cert

Windows & Light

Construction Studies - Leaving Cert

Wood, rot & Ventilation

Construction Studies - Leaving Cert

Air Tightness & Condensation

Construction Studies - Leaving Cert

Concrete

Construction Studies - Leaving Cert

Fire Places & Fire Prevention

Construction Studies - Leaving Cert

Foundations, Floors & Walls

Construction Studies - Leaving Cert

Question One Drawing Questions

Construction Studies - Leaving Cert

Services, Water, Gas, Electrical

Construction Studies - Leaving Cert

Windows & Doors

Construction Studies - Leaving Cert

;