The external wall of a house built in the 1990s is of 100 mm concrete block construction with a 100 mm partially filled cavity, as shown - Leaving Cert Construction Studies - Question 5 - 2019
Question 5
The external wall of a house built in the 1990s is of 100 mm concrete block construction with a 100 mm partially filled cavity, as shown.
(a) Calculate the U-value ... show full transcript
Worked Solution & Example Answer:The external wall of a house built in the 1990s is of 100 mm concrete block construction with a 100 mm partially filled cavity, as shown - Leaving Cert Construction Studies - Question 5 - 2019
Step 1
Calculate the U-value of the wall
96%
114 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
To calculate the U-value of the wall, we first need to find the total resistance (R) of each layer and then apply the formula for U-value.
Resistance Calculation:
External Render:
Thickness = 0.016 m,
Resistivity = 0.048 m² °C/W.
Concrete Block Outer Leaf:
Thickness = 0.1 m,
Conductivity = 1.440 W/m °C.
Clear Cavity:
Resistance = 0.170 m² °C/W.
Polystyrene Insulation:
Thickness = 0.1 m,
Conductivity = 0.037 W/m °C.
Concrete Block Inner Leaf:
Thickness = 0.1 m,
Conductivity = 1.440 W/m °C.
Internal Plaster:
Thickness = 0.012 m,
Conductivity = 6.250 W/m °C.
Internal Surface Resistance:
R = 0.012 m² °C/W.
Total Resistance Calculation:
Using the resistances:
Rtotal=Rexternal+Router+Rcavity+Rinsulation+Rinner+Rplaster+Rinternal
To find U-value:
U=Rtotal1
Calculating this gives us:
Rtotal=0.048+0.069+0.170+2.703+0.069+0.005+0.012
Conclusively, calculating yields:
U=0.516m2°CW
Step 2
Using the U-value obtained at 5(a) calculate cost of heat loss
99%
104 rated
Only available for registered users.
Sign up now to view full answer, or log in if you already have an account!
Answer
The heat loss through the wall can be calculated using:
Heat Loss Formula:
Heat loss=U×Area×Temp. diff.
Given Values:
U-value = 0.516 W/m²°C
Area = 135 m²
Temperature difference = (19 - 5) °C = 14 °C
Calculation:
Heat loss per second:
Heat loss=0.516×135×14
This results in:
975.24Watts
Heat input in heating hours:
Total heating period = 60 hours × 36 weeks = 2168 hours.
Total heat loss condenses to:
Total Loss=975.24×2168
Divide by 1000 to convert to kW:
1000Total Loss
Cost Calculation with caloric values gives:
Therefore:
Cost=212.34×0.94
Final Cost Affiliation leads to about £199.60 annually.